Unbalanced 3 Phase Equipment Load


  • Please log in to reply
1 reply to this topic

#1 Lanny Purvis PE

Lanny Purvis PE

    Member

  • Member
  • PipPip
  • 19 posts

Posted 09 March 2017 - 01:55 PM

I am creating a design with a Vulcan Heavy Duty Electric Griddle.  It is a model number HEG48E.  The oddball thing about this piece of equipment is that it connects 10.8KW from phase A to B, 5.4KW from B to C, and 5.4KW from C to A.  The equipment voltage is 208 3 phase four wire.  How do I model this under the equipment tab?

Lanny

#2 David Robison

David Robison

    Design Master Software

  • Admin
  • PipPipPip
  • 1,299 posts
  • Gender:Male
  • Location:Raleigh, NC

Posted 13 March 2017 - 05:21 AM

You have to model this as two pieces of equipment. A three phase connection at 16.2 kW, then a single phase connection at 5.4 kW. Connect the three phase connection to the circuit, then use the "Circuit to Phase" button to connect the single phase connection to phase A.